Mark and Susan Miller wrote:
> I need some help that I'm sure this list can provide. Our furnace won't come
> on. It's a fraser-johnson with a White Rodgers 50A50-241 controller.
>
> The blower will come on if set to 'fan on' via the thermostat. I verified
> that the thermostat is OK (read a closed circuit at the furnace where the
> control signals come in, also put jumpers on at the t'stat and then at the
> furnace and still no change). There is a fan that appears to be to boost the
> exhaust up the chimney - it comes on. There is an LED on the controller that
> gives three blinks. I'm guessing a sensor is either telling me something is
> wrong or has failed.
>
> Anyone know where I can find a control schematic for this thing? The
> White-Rodgers site has a link to one but it doesn't come up (browser says it
> isn't there).
White-Rodgers isn't very helpful with older products, are they? But, this might
be a workaround. I went to their site,
searched for an equivalent current product and got the sheet for that:
http://www.white-rodgers.com/pdfs/instruction_sheets/0037-6265.pdf
According to this, three flashes indicates that the pressure switch is stuck
open, so you might look at that, and check
the wiring between the controller and the switch.
Cheers.
--