At 21:26 7/1/96 -0500, Ed Mulligan wrote:
>Let's see if I can send to this list. . .
>
>All this talk about dryer cords and grounding got me wondering.  I dug out 
>the 1996 NEC, and an article 
>about the new 1996 NEC changes, and my 1996 NEC class notes, and the 1993 
>NEC Handbook.  From 
>SNIP

Ed:
     Thanks for the info.  Seems like I have to go out and buy a new copy of
the NEC now. :-) This change was LONG overdue.  I would equate this to the
sea change that required grounded plugs on 110 volt residential circuits.  I
have not seen the new 4 wire plugs and receptacles, but as soon as they hit
my local area, I am going to retrofit my 220 volt appliances - grandfathered
or not!  Safety comes above a few bucks and a flimsy 18 guage green wire!
Will also make 110 and 220 volt wiring practices consistent and more easily
understood by electricians.

SNIP
this I would guess that the reason your dryer has no separate ground wire is 
>that the NEC didn't require it at the time.  As I see it, the dryer is OK 
>(grandfathered under the revised for 
>1996 section 250-60) and the air compressor would never be legal connected 
>the same way (section 250-
>61(b)). 
>           --------------------------------------------------------------------
>From Electrical Contractor magazine, 9/95 
> ARTICLE 250 - GROUNDING 
>Ranges, Dryers, and Ovens Now Require Four-Wire Receptacles and Cords 
>Section 250-60 Clarify intent of Code 
>The code no longer permits the grounded circuit conductor (neutral) to 
>ground the frame or junction box 
>of electric ranges, wall-mounted ovens, counter-mounted cooking units, 
>clothes dryers for "new 
>installations."  Note:  This change brings the NEC into alignment with the 
>Canadian Electrical Code, 
>which has always required four-wire supply cords for these appliances. 
>There is an illustration showing: 
> "Proper Installation" = a 4-prong receptacle with the 3-prongs straight up 
>and down, and a half round 
>ground pin (like a regular 3-prong 110V outlet, but with an additional slot).  
>VIOLATION = the three prong receptacle with the neutral connected to the 
>grounded conduit system at 
>the receptacle box. 
>           --------------------------------------------------------------------
>According to Gregory P. Bierals (my employer brings him in to explain the 
>changes to the code every 
>three years - he's the only man I've ever met that has actually memorized 
>the NEC.  Ask him a question, 
>and he'll tell you the answer, the section the answer is from, and often the 
>page number it appears on in 
>the paperback edition.) "A significant modification has been made to Section 
>250-60 with regard to the 
>use of the grounded conductor (neutral) for the purpose of grounding the 
>frame. . .  This provision will 
>only apply to existing installations and not to new branch-circuit 
>installations which will require an 
>equipment grounding conductor routed with the branch-circuit conductors as 
>the equipment grounding 
>means." 
>           --------------------------------------------------------------------
>Why did the code allow this in the past?  This is from  the 1993 NEC Handbook:
>"The use of the grounded circuit conductor for grounding purposes is 
>contrary to other sections of the 
>Code. . .  However, it has been allowed for many years because of the good 
>safety record of those 
>appliances that are grounded through the grounded circuit conductor and 
>because an open splice or break 
>in the grounded circuit conductor would normally render the appliance 
>inoperable.  A subcommittee 
>reevaluated this requirement for the 1984 NEC and verified the continued 
>good safety record."  It goes on 
>to explain exactly what would happen if this wiring practice should fail - 
>fire/injury/death.  
>           --------------------------------------------------------------------
>What does section 250-61(b) say?
>"Load-Side Equipment.  A grounded circuit conductor shall not be used for 
>grounding noncurrent-
>carrying metal parts of equipment on the load side of the service 
>disconnecting means or on the load side 
>of a separately derived system disconnecting means or the overcurrent 
>devices for a separately derived 
>system no having a main disconnecting means."  It lists 5 exceptions - none 
>apply to your air compressor.
>           --------------------------------------------------------------------
>My $0.02: 
>** As always, check this with an actual residential electrician.**  We don't 
>wire too many dryers or ovens 
>in our manufacturing facilities, so I'm no expert. 
>I've always understood existing installations to be grandfathered, until you 
>start to work on them.  If you 
>make a change, you have to bring everything up to current code spec.  So 
>right now, your dryer should be 
>legal. Connecting the air compressor this way would violate section 
>250-61(b).  Spring for a new circuit 
>breaker and outlet.  Parts and labor are cheap compared to people and 
>equipment.  
>If the compressor is portable, or at least able to move, I'd use a 
>twist-lock plug and receptacle as well.  I'd 
>hate to be there if the plug gets pulled out or plugged in with the motor 
>on.  Besides, it promotes domestic 
>harmony to not have the cars interfere with the laundry. 
> 
>Ed 
>
> 
>Ed & Laura Mulligan     mulligan@fullnet.net    
> http://www.fullnet.net/user/mulligan