All this talk about dryer cords and grounding got me wondering.  I dug out 
the 1996 NEC, and an article 
about the new 1996 NEC changes, and my 1996 NEC class notes, and the 1993 
NEC Handbook.  From 
this I would guess that the reason your dryer has no separate ground wire is 
that the NEC didn't require it at the time.  As I see it, the dryer is OK 
(grandfathered under the revised for 
1996 section 250-60) and the air compressor would never be legal connected 
the same way (section 250-
61(b)). 
           --------------------------------------------------------------------
>From Electrical Contractor magazine, 9/95 
 ARTICLE 250 - GROUNDING 
Ranges, Dryers, and Ovens Now Require Four-Wire Receptacles and Cords 
Section 250-60 Clarify intent of Code 
The code no longer permits the grounded circuit conductor (neutral) to 
ground the frame or junction box 
of electric ranges, wall-mounted ovens, counter-mounted cooking units, 
clothes dryers for "new 
installations."  Note:  This change brings the NEC into alignment with the 
Canadian Electrical Code, 
which has always required four-wire supply cords for these appliances. 
There is an illustration showing: 
 "Proper Installation" = a 4-prong receptacle with the 3-prongs straight up 
and down, and a half round 
ground pin (like a regular 3-prong 110V outlet, but with an additional slot).  
VIOLATION = the three prong receptacle with the neutral connected to the 
grounded conduit system at 
the receptacle box. 
           --------------------------------------------------------------------
According to Gregory P. Bierals (my employer brings him in to explain the 
changes to the code every 
three years - he's the only man I've ever met that has actually memorized 
the NEC.  Ask him a question, 
and he'll tell you the answer, the section the answer is from, and often the 
page number it appears on in 
the paperback edition.) "A significant modification has been made to Section 
250-60 with regard to the 
use of the grounded conductor (neutral) for the purpose of grounding the 
frame. . .  This provision will 
only apply to existing installations and not to new branch-circuit 
installations which will require an 
equipment grounding conductor routed with the branch-circuit conductors as 
the equipment grounding 
means." 
           --------------------------------------------------------------------
Why did the code allow this in the past?  This is from  the 1993 NEC Handbook:
"The use of the grounded circuit conductor for grounding purposes is 
contrary to other sections of the 
Code. . .  However, it has been allowed for many years because of the good 
safety record of those 
appliances that are grounded through the grounded circuit conductor and 
because an open splice or break 
in the grounded circuit conductor would normally render the appliance 
inoperable.  A subcommittee 
reevaluated this requirement for the 1984 NEC and verified the continued 
good safety record."  It goes on 
to explain exactly what would happen if this wiring practice should fail - 
fire/injury/death.  
           --------------------------------------------------------------------
What does section 250-61(b) say?
"Load-Side Equipment.  A grounded circuit conductor shall not be used for 
grounding noncurrent-
carrying metal parts of equipment on the load side of the service 
disconnecting means or on the load side 
of a separately derived system disconnecting means or the overcurrent 
devices for a separately derived 
system no having a main disconnecting means."  It lists 5 exceptions - none 
apply to your air compressor.
           --------------------------------------------------------------------
My $0.02: 
** As always, check this with an actual residential electrician.**  We don't 
wire too many dryers or ovens 
in our manufacturing facilities, so I'm no expert. 
I've always understood existing installations to be grandfathered, until you 
start to work on them.  If you 
make a change, you have to bring everything up to current code spec.  So 
right now, your dryer should be 
legal. Connecting the air compressor this way would violate section 
250-61(b).  Spring for a new circuit 
breaker and outlet.  Parts and labor are cheap compared to people and 
equipment.  
If the compressor is portable, or at least able to move, I'd use a 
twist-lock plug and receptacle as well.  I'd 
hate to be there if the plug gets pulled out or plugged in with the motor 
on.  Besides, it promotes domestic 
harmony to not have the cars interfere with the laundry. 
 
Ed 

 
Ed & Laura Mulligan     mulligan@fullnet.net    
 http://www.fullnet.net/user/mulligan
'92 5.0 LX    "I love the sound of Flowmasters in the morning!"
 MOUSE:   "You're immune to both romance and mirth, you must be a. . . a. . ."
 DILBERT:    "That's right.  I'm an engineer."

   


<Prev in Thread] Current Thread [Next in Thread>
  • What the NEC has to say about the whole compressor/dryer mess, Ed Mulligan <=