I need to run a 50amp circuit about 50 or 60 feet.
A calculator on the web says that 55' of 50amp circuit would require 10#
wire. Does that sound right? Anyone know what the code states?
>>>
I'm not sure you got the answer you were looking for but I just looked in
the NEC (old, 1999 version, but this stuff stays pretty much the same table
B-310-1) and the table reads that with THHN wire in a conduit you'd need at
least 6 gauge wire. 8ga maxes out at 48 amps, 6ga at 65 amps. For direct
burial cable you can use 8ga.
The limits are based on temperature rise; there is much better heat flow
away from a buried cable than one in a conduit.
The calculator will give you the info for voltage drops, but you still must
meet the minimum wire gauge for the current.
Mark not a licensed electrician Miller
|